Posted 7/24/2006 3:07:58 PM Post #543
Anonymous 
I have a brand new indoor pool that is approximately 25x40 in the Catskills (Upstate New York). We keep the water at about 84F and the indoor temp at about 78F. We have (2) outside dampers that open and then bring on two exhaust fans to ventilate the room (70x50 w/ 17' ceilings) when the indoor R.H. reaches 70%. There is an outdoor humidistat that shuts this down if the outdoor R.H. is above 85%. We also have a 3-ton hydroair system with underground ductwork running along the perimeter blowing out of the floor under windows. We also have a 7.5 ton straight a/c system with a high supply/ low return setup on one gable end wall. What do you think of this set-up/design? What could we do better/ different?
Posted 1/2/2007 5:40:33 PM Post #544
 

Supreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme BeingSupreme Being
Your system should work well when the outdoor dew points <50^F. High outdoor dew points with moderate weather leaves the inside wet. A couple days of damp weather may be ok. A wet week or two will be a problem without a method of drying. Your concept is ideal for arrid climates like Arizona.
Covering the pool with plastic and Hi-Dry 195 Vehere could be a solution for occasional extended high dew point conditions. http://www.thermastor.com/prod_poolspa.htm

Thanks for an interesting post. Ken
« Prev Topic | Next Topic »


Reading This Topic Expand / Collapse
Active Users: 0 (0 guests, 0 members, 0 anonymous members)
No members currently viewing this topic.

Permissions Expand / Collapse

All times are GMT -6:00, Time now is 6:29am

Therma-Stor Forum Home Page  |  ThermaStor.com Home Page

Copyright © 2008 Therma-Stor LLC